Does LIGHT version support IEEE Float data?

I am trying to connect to Watlow F4T process controller. Its temperature setpoint is IEEE float, 2 registers. After testing, I found it is using BADC reversed IEEE. I chose Open Modbus TCP and Reverse IEEE Double Byte, but I don’t get the correct value. I tried both relative and absolute addresses, but neither worked. Could someone help me with it? Or the LIGHT version doesn’t support 2-register data?

Thank you

Did you append “/float” to the address?

https://www.vtscada.com/help/Content/D_Tags/Dev_DataSuffixesForTagIO.htm

https://www.vtscada.com/help/Content/D_Tags/Dev_ModiconTags.htm